      I have a 8yr old American Standard 90% effecient furnace that after the unit reaches it’s preset warm up temp. and starts actually blowing the warm air, shuts off after only a couple of seconds and starts cycling through almost continually. I added 15′ of pvc exhaust pipe to move it from under a deck I built and was wondering if that could have thing to do with it by possibly retarding the exhaust air flow.

    • #121560
      Harold hydronicnetwork.net
      Guest

      Yes, adding the pipe can affect the operation that way. Read the manufacturer’s installation sheet for the maximum length and size of the tubing. you might be able to install 4-inch instead of 3-inch if the instructions permit.