    • #10675
      tom
      Guest

      Can I vent an upper bath into an attic crawl space(insulated)? The attic runs the length of the house with ridge vent plus two 12×12 louvered vents in each peak. Also, the bath measures 10×10 ft. with a ceiling sloping from seven feet to five feet. What is the minimum size fan will I need? Thanks for all your advice.

    • #76497
      JT
      Guest

      tom, venting into the attic is a bad idea and against
      most (probably all) model building codes. If you don’t
      want to go through your ceiling, maybe a through-the-wall
      model would work for you.
      I believe the minimum volume called for by the UBC is
      5 air changes per hour, but 8 is more commonly used.
      The volume of your bathroom is 600 cu. ft., so
      (600 x 8)/60 = 80 cfm. I think Panasonic makes a 90
      cfm. (check http://www.tamtech.com). You should be aware that
      bath fans don’t have a lot of power behind them, so
      you need to keep ducting as short as possible, and
      make all bends as gradual as possible. If your duct
      path gets nasty, you will have to go to a larger model
      to get the cfm you need.